CygNet Measurement > Using CygNet Measurement > Required Device Configuration Items

Required Device Configuration Data Items for CygNet Measurement

Devices must be configured to contain certain minimum required data items to function successfully in CygNet Measurement. Various device and calculation types have specific configuration data requirements in order to operate with CygNet Measurement to achieve the desired calculation functionality in your system. For instance, devices that were previously configured for Gas Measurement Repository (GMR) systems can be utilized by CygNet Measurement (FMS) systems if they are configured to contain the required "FMS" or "FMS Legacy" data items.

Note: If you are preparing to migrate data from GMR to FMS, certain data items do not migrate. See Configuration Data Items that Do Not Migrate from GMR to FMS and History Data Items that Do Not Migrate from GMR to FMS for more information.

Required Data Items

The terms "output" and "input" used in the sections below are relative to the calculation.

Output Data Items

The following (output) FMS data items will be calculated by the system if not provided by the device. In cases where volume is provided, the system will calculate a volume value for comparison with the device-provided volume and create a VCF value. See VCF for more information.

See corresponding data items lists in the EFM Data Items section for more information.

Input Data Items

The following tables list historical and configuration (input) FMS data items that are required to be present in your devices in order to successfully use FMS. Data items that are required to be present, but for which values are optional, are listed as "Optional" in the Input Required column. The tables are arranged according to calculation/device types, and contain the data item description, data item input requirements, the FMS data item string, the corresponding FMS Legacy (eGMR_...) data item string where applicable, and links to additional helpful information about specific device data items and their possible values.

AGA-3 1985 (Orifice)

The following data items are required for AGA 3-1985 calculations for orifice devices.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
Atmospheric Pressure Required if SP Sensor Type = Gauge eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Calibration Factor Optional eFMS_CFG_CALIBRATION_FACTOR eGMR_CFG_CALIBRATION_FACTOR
DP Taps Type Required eFMS_CFG_DP_TAPS_TYPE eGMR_CFG_DP_TAPS_TYPE
Fluid Type Optional eFMS_CFG_FLUID_TYPE eGMR_CFG_FLUID_TYPE
Heating Value - Volume Required if corresponding history item is missing eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Integral Value Variable Optional eFMS_CFG_INTEGRAL_VALUE_VARIABLES (No corresponding data item)
Isentropic Exponent Optional eFMS_CFG_ISENTROPIC_EXPONENT eGMR_CFG_ISENTROPIC_EXPONENT
Low Flow Cutoff - DP (differential pressure) Optional eFMS_CFG_LOW_FLOW_CUTOFF_DP eGMR_CFG_LOW_FLOW_CUTOFF_DP
Low Flow Cutoff - Flow Rate (volume flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE eGMR_CFG_LOW_FLOW_CUTOFF_FLOW_RATE
Meter Factor Optional eFMS_CFG_METER_FACTOR eGMR_CFG_METER_CORRECTION_FACTOR
Meter Tube Inside Diameter Required eFMS_CFG_METER_TUBE_INSIDE_DIAMETER eGMR_CFG_INSIDE_PIPE_DIAMETER
Meter Tube Material Required to have a valid value (not Unspecified) if Pipe Thermal Expansion Coefficient is missing eFMS_CFG_METER_TUBE_MATERIAL eGMR_CFG_PIPE_MATERIAL
Meter Tube Reference Temperature Required eFMS_CFG_METER_TUBE_REF_TEMP eGMR_CFG_INSIDE_PIPE_DIAMETER_MEASURE_TEMP
Orifice Plate Bore Size Required eFMS_CFG_ORIFICE_PLATE_BORE_SIZE eGMR_CFG_ORIFICE_DIAMETER
Orifice Plate Material Required to have a valid value (not Unspecified) if Orifice Thermal Expansion Coefficient is missing eFMS_CFG_ORIFICE_PLATE_MATERIAL eGMR_CFG_ORIFICE_PLATE_MATERIAL
Orifice Plate Reference Temperature Required eFMS_CFG_ORIFICE_PLATE_REF_TEMP eGMR_CFG_ORIFICE_DIAMETER_MEASURE_TEMP
Orifice Thermal Expansion Coefficient Required if Orifice Plate Material = Unspecified eFMS_CFG_ORIFICE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_ORIFICE_EXPANSION_FACTOR
Pipe Thermal Expansion Coefficient Required if Meter Tube Material = Unspecified eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_PIPE_EXPANSION_FACTOR
Relative Density Required; if an hourly history value is present, that value will be used instead of the configuration value eFMS_CFG_RELATIVE_DENSITY eGMR_CFG_SPECIFIC_GRAVITY
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
SP Tap Location Required eFMS_CFG_SP_TAP_LOCATION eGMR_CFG_SP_TAP_LOCATION
Standard Air Compressibility Optional eFMS_CFG_BASE_COMPRESSIBILITY_OF_AIR eFMS_CFG_STANDARD_AIR_COMPRESSIBILITY
Viscosity Required; if an hourly history value is present, that value will be used instead of the configuration value eFMS_CFG_VISCOSITY eGMR_CFG_VISCOSITY
Water Vapor Correction Factor Optional eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR eGMR_CFG_CALC_WATER_VAPOR_CORRECTION_FACTOR
Well Stream Factor Optional eFMS_CFG_WELL_STREAM_FACTOR eGMR_CFG_WELL_STREAM_FACTOR
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Differential Pressure (DP) Required if Integral Value is missing eFMS_PV_DIFF_PRESSURE eGMR_PROCESS_VAR_DIFF_PRESSURE
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Flow Time Required eFMS_PV_FLOW_TIME eGMR_PROCESS_VAR_FLOW_TIME
Heating Value - Volume Required eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Integral Value Required if Differential Pressure is missing eFMS_PV_IV eGMR_PROCESS_VAR_SUM_OF_EXTENSIONS
Meter Factor Optional eFMS_PV_METER_FACTOR eGMR_PROCESS_VAR_METER_FACTOR
Relative Density Required if corresponding configuration item is missing eFMS_PV_RELATIVE_DENSITY eGMR_PROCESS_VAR_SPECIFIC_GRAVITY
Static Pressure (SP) (Line Pressure) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Viscosity Required if corresponding history item is missing eFMS_PV_VISCOSITY eGMR_PROCESS_VAR_VISCOSITY
Back to top

AGA-3 1992 (Orifice)

The following data items are required for AGA 3-1992 calculations for orifice devices.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they are used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
AGA 3 Expanded Range Optional eFMS_CFG_AGA3_EXPANDED_RANGE eGMR_CFG_AGA3_EXPANDED_RANGE
Atmospheric Pressure Required if SP Sensor Type = Gauge eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Calibration Factor Optional eFMS_CFG_CALIBRATION_FACTOR eGMR_CFG_CALIBRATION_FACTOR
DP Taps Type Required eFMS_CFG_DP_TAPS_TYPE eGMR_CFG_DP_TAPS_TYPE
Fluid Type Optional eFMS_CFG_FLUID_TYPE eGMR_CFG_FLUID_TYPE
Heating Value - Volume Required if corresponding history item is missing eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Integral Value Variable Optional eFMS_CFG_INTEGRAL_VARIABLE_VARIABLES (No corresponding data item)
Isentropic Exponent Optional eFMS_CFG_ISENTROPIC_EXPONENT eGMR_CFG_ISENTROPIC_EXPONENT
Low Flow Cutoff - DP (differential pressure) Optional eFMS_CFG_LOW_FLOW_CUTOFF_DP eGMR_CFG_LOW_FLOW_CUTOFF_DP
Low Flow Cutoff - Flow Rate (volume flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE eGMR_CFG_LOW_FLOW_CUTOFF_FLOW_RATE
Meter Factor Optional eFMS_CFG_METER_FACTOR eGMR_CFG_METER_CORRECTION_FACTOR
Meter Tube Inside Diameter Required eFMS_CFG_METER_TUBE_INSIDE_DIAMETER eGMR_CFG_INSIDE_PIPE_DIAMETER
Meter Tube Material Required to have a valid value (not Unspecified) if Pipe Thermal Expansion Coefficient is missing eFMS_CFG_METER_TUBE_MATERIAL eGMR_CFG_PIPE_MATERIAL
Meter Tube Reference Temperature Required eFMS_CFG_METER_TUBE_REF_TEMP eGMR_CFG_INSIDE_PIPE_DIAMETER_MEASURE_TEMP
Orifice Plate Bore Size Required eFMS_CFG_ORIFICE_PLATE_BORE_SIZE eGMR_CFG_ORIFICE_DIAMETER
Orifice Plate Material Required to have a valid value (not Unspecified) if Orifice Thermal Expansion Coefficient is missing eFMS_CFG_ORIFICE_PLATE_MATERIAL eGMR_CFG_ORIFICE_PLATE_MATERIAL
Orifice Plate Reference Temperature Required eFMS_CFG_ORIFICE_PLATE_REF_TEMP eGMR_CFG_ORIFICE_DIAMETER_MEASURE_TEMP
Orifice Thermal Expansion Coefficient Required if Orifice Plate Material = Unspecified eFMS_CFG_ORIFICE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_ORIFICE_EXPANSION_FACTOR
Pipe Thermal Expansion Coefficient Required if Meter Tube Material = Unspecified eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_PIPE_EXPANSION_FACTOR
Relative Density Required; if an hourly history value is present, that value will be used instead of the configuration value eFMS_CFG_RELATIVE_DENSITY eGMR_CFG_SPECIFIC_GRAVITY
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
SP Tap Location Required eFMS_CFG_SP_TAP_LOCATION eGMR_CFG_SP_TAP_LOCATION
Standard Air Compressibility Optional eFMS_CFG_BASE_COMPRESSIBILITY_OF_AIR eFMS_CFG_STANDARD_AIR_COMPRESSIBILITY
Viscosity Required; if an hourly history value is present, that value will be used instead of the configuration value eFMS_CFG_VISCOSITY eGMR_CFG_VISCOSITY
Water Vapor Correction Factor Optional eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR eGMR_CFG_CALC_WATER_VAPOR_CORRECTION_FACTOR
Well Stream Factor Optional eFMS_CFG_WELL_STREAM_FACTOR eGMR_CFG_WELL_STREAM_FACTOR
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Differential Pressure (DP) Required if Integral Value is missing eFMS_PV_DIFF_PRESSURE eGMR_PROCESS_VAR_DIFF_PRESSURE
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Flow Time Required eFMS_PV_FLOW_TIME eGMR_PROCESS_VAR_FLOW_TIME
Heating Value - Volume Required if corresponding configuration item is missing eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Integral Value Required if Differential Pressure is missing eFMS_PV_IV eGMR_PROCESS_VAR_SUM_OF_EXTENSIONS
Meter Factor Optional eFMS_PV_METER_FACTOR eGMR_PROCESS_VAR_METER_FACTOR
Relative Density Required if corresponding configuration item is missing eFMS_PV_RELATIVE_DENSITY eGMR_PROCESS_VAR_SPECIFIC_GRAVITY
Static Pressure (SP) (Line Pressure) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Viscosity Required if corresponding configuration item is missing eFMS_PV_VISCOSITY eGMR_PROCESS_VAR_VISCOSITY
Back to top

AGA-3 2013 (Orifice)

The following data items are required for AGA 3-2013 calculations for orifice devices.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they are used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
AGA 3 Expanded Range Optional eFMS_CFG_AGA3_EXPANDED_RANGE eGMR_CFG_AGA3_EXPANDED_RANGE
Atmospheric Pressure Required if SP Sensor Type = Gauge eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Calibration Factor Optional eFMS_CFG_CALIBRATION_FACTOR eGMR_CFG_CALIBRATION_FACTOR
DP Taps Type Required eFMS_CFG_DP_TAPS_TYPE eGMR_CFG_DP_TAPS_TYPE
Fluid Type Optional eFMS_CFG_FLUID_TYPE eGMR_CFG_FLUID_TYPE
Heating Value - Volume Required if corresponding history item is missing eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Integral Value Variable Optional eFMS_CFG_INTEGRAL_VARIABLE_VARIABLES (No corresponding data item)
Isentropic Exponent Optional eFMS_CFG_ISENTROPIC_EXPONENT eGMR_CFG_ISENTROPIC_EXPONENT
Low Flow Cutoff - DP (differential pressure) Optional eFMS_CFG_LOW_FLOW_CUTOFF_DP eGMR_CFG_LOW_FLOW_CUTOFF_DP
Low Flow Cutoff - Flow Rate (volume flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE eGMR_CFG_LOW_FLOW_CUTOFF_FLOW_RATE
Meter Factor Optional eFMS_CFG_METER_FACTOR eGMR_CFG_METER_CORRECTION_FACTOR
Meter Tube Inside Diameter Required eFMS_CFG_METER_TUBE_INSIDE_DIAMETER eGMR_CFG_INSIDE_PIPE_DIAMETER
Meter Tube Material Required to have a valid value (not Unspecified) if Pipe Thermal Expansion Coefficient is missing eFMS_CFG_METER_TUBE_MATERIAL eGMR_CFG_PIPE_MATERIAL
Meter Tube Reference Temperature Required eFMS_CFG_METER_TUBE_REF_TEMP eGMR_CFG_INSIDE_PIPE_DIAMETER_MEASURE_TEMP
Orifice Plate Bore Size Required eFMS_CFG_ORIFICE_PLATE_BORE_SIZE eGMR_CFG_ORIFICE_DIAMETER
Orifice Plate Material Required to have a valid value (not Unspecified) if Orifice Thermal Expansion Coefficient is missing eFMS_CFG_ORIFICE_PLATE_MATERIAL eGMR_CFG_ORIFICE_PLATE_MATERIAL
Orifice Plate Reference Temperature Required eFMS_CFG_ORIFICE_PLATE_REF_TEMP eGMR_CFG_ORIFICE_DIAMETER_MEASURE_TEMP
Orifice Thermal Expansion Coefficient Required if Orifice Plate Material = Unspecified eFMS_CFG_ORIFICE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_ORIFICE_EXPANSION_FACTOR
Pipe Thermal Expansion Coefficient Required if Meter Tube Material = Unspecified eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_PIPE_EXPANSION_FACTOR
Relative Density Required; if an hourly history value is present, that value will be used instead of the configuration value eFMS_CFG_RELATIVE_DENSITY eGMR_CFG_SPECIFIC_GRAVITY
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
SP Tap Location Required eFMS_CFG_SP_TAP_LOCATION eGMR_CFG_SP_TAP_LOCATION
Standard Air Compressibility Optional eFMS_CFG_BASE_COMPRESSIBILITY_OF_AIR eFMS_CFG_STANDARD_AIR_COMPRESSIBILITY
Viscosity Required; if an hourly history value is present, that value will be used instead of the configuration value eFMS_CFG_VISCOSITY eGMR_CFG_VISCOSITY
Water Vapor Correction Factor Optional eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR eGMR_CFG_CALC_WATER_VAPOR_CORRECTION_FACTOR
Well Stream Factor Optional eFMS_CFG_WELL_STREAM_FACTOR eGMR_CFG_WELL_STREAM_FACTOR
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Differential Pressure (DP) Required if Integral Value is missing eFMS_PV_DIFF_PRESSURE eGMR_PROCESS_VAR_DIFF_PRESSURE
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Flow Time Required eFMS_PV_FLOW_TIME eGMR_PROCESS_VAR_FLOW_TIME
Heating Value - Volume Required if corresponding configuration item is missing eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Integral Value Required if Differential Pressure is missing eFMS_PV_IV eGMR_PROCESS_VAR_SUM_OF_EXTENSIONS
Meter Factor Optional eFMS_PV_METER_FACTOR eGMR_PROCESS_VAR_METER_FACTOR
Relative Density Required if corresponding configuration item is missing eFMS_PV_RELATIVE_DENSITY eGMR_PROCESS_VAR_SPECIFIC_GRAVITY
Static Pressure (SP) (Line Pressure) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Viscosity Required if corresponding configuration item is missing eFMS_PV_VISCOSITY eGMR_PROCESS_VAR_VISCOSITY
Back to top

AGA-7 (Turbine/Ultrasonic)

The following data items are required for AGA 7 calculations for turbine or ultrasonic devices.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
Atmospheric Pressure Required if SP Sensor Type = Gauge eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Calibration Factor Optional eFMS_CFG_CALIBRATION_FACTOR eGMR_CFG_CALIBRATION_FACTOR
Fluid Type Optional eFMS_CFG_FLUID_TYPE eGMR_CFG_FLUID_TYPE
Heating Value - Volume Required if corresponding history item is missing eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Low Flow Cutoff - Pulse Interval Optional eFMS_CFG_LOW_FLOW_CUTOFF_PULSE_INTERVAL eGMR_CFG_LOW_FLOW_CUTOFF_PULSES
Low Flow Cutoff - Flow Rate (volume flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE eGMR_CFG_LOW_FLOW_CUTOFF_FLOW_RATE
Meter Factor Required if corresponding history item is missing eFMS_CFG_METER_FACTOR eGMR_CFG_METER_CORRECTION_FACTOR
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
Water Vapor Correction Factor Optional eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR eGMR_CFG_CALC_WATER_VAPOR_CORRECTION_FACTOR
Well Stream Factor Optional eFMS_CFG_WELL_STREAM_FACTOR eGMR_CFG_WELL_STREAM_FACTOR
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Flow Time Optional eFMS_PV_FLOW_TIME eGMR_PROCESS_VAR_FLOW_TIME
Heating Value - Volume Required if corresponding configuration item is missing eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Linear Integral Value Required if Pulses is missing eFMS_PV_LINEAR_IV (No corresponding data item)
K Factor - Volume Required eFMS_CFG_GAS_K_FACTOR_VOLUME

(previously eFMS_CFG_K_FACTOR)

eGMR_CFG_PULSES_PER_SCF
K Factor Required (No corresponding data item) eGMR_PROCESS_VAR_K_FACTOR
Meter Factor Required if corresponding configuration item is missing eFMS_PV_METER_FACTOR eGMR_PROCESS_VAR_METER_FACTOR
Pulses (Pulse Count) Required if Linear Integral Value is missing eFMS_PV_PULSES eGMR_PROCESS_VAR_PULSES
Static Pressure (SP) (Line Pressure) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Back to top

AGA-11 (Coriolis)

The following data items are required for AGA 11 calculations for coriolis devices.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
Atmospheric Pressure Required if both of the following are true.
  • SP Sensor Type = Absolute
  • Compressibility Calculation = AGA 8 Method Gross 1, Gross 2, or Detail Complete
eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required if Fluid Type = Noncompressible eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required if Fluid Type = Noncompressible eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Calibration Static Pressure Required if Flowing Pressure Effect is valid eFMS_CFG_CORIOLIS_CALIBRATION_PRESSURE eGMR_CFG_CORIOLIS_CALIBRATION_PRESSURE
Flowing Pressure Effect Required if Use Coriolis Pressure Effect = True eFMS_CFG_CORIOLIS_PRESSURE_EFFECT eGMR_CFG_CORIOLIS_FLOWING_PRESSURE_EFFECT
Fluid Type Optional eFMS_CFG_FLUID_TYPE eGMR_CFG_FLUID_TYPE
Heating Value - Mass Required if corresponding history item is missing

Required for Energy calculations

eFMS_CFG_HEATING_VALUE_MASS (No corresponding data item)
Heating Value - Volume Required if corresponding history item is missing

Required for Energy calculations; if mass value is missing, will use Heating Value Volume instead of Heating Volume Mass

eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Linear Curve Type Required eFMS_CFG_LINEAR_CURVE_TYPE eGMR_CFG_CORIOLIS_CURVE_TYPE
Low Flow Cutoff - Flow Rate (volume flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE eGMR_CFG_LOW_FLOW_CUTOFF_FLOW_RATE
Low Flow Cutoff - Mass (mass flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_MASS (No corresponding data item)
Low Flow Cutoff - Pulses (pulse interval) Optional eFMS_CFG_LOW_FLOW_CUTOFF_PULSE_INTERVAL eGMR_CFG_LOW_FLOW_CUTOFF_PULSES
Meter Factor Required if Integral Value is missing eFMS_CFG_METER_FACTOR eGMR_CFG_METER_CORRECTION_FACTOR
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
Use Coriolis Pressure Effect Optional eFMS_CFG_USE_CORIOLIS_PRESSURE_EFFECT eGMR_CFG_CORIOLIS_FLOWING_PRESSURE_ENABLED
Water Vapor Correction Factor Optional eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR eGMR_CFG_CALC_WATER_VAPOR_CORRECTION_FACTOR
Well Stream Factor Optional eFMS_CFG_WELL_STREAM_FACTOR eGMR_CFG_WELL_STREAM_FACTOR
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Flow Time Required eFMS_PV_FLOW_TIME eGMR_PROCESS_VAR_FLOW_TIME
Heating Value - Volume Optional eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Heating Value - Mass Optional eFMS_PV_HEATING_VALUE_MASS (No corresponding data item)
Integral Value Required if Pulses is missing eFMS_PV_IV eGMR_PROCESS_VAR_SUM_OF_EXTENSIONS
K Factor - Volume Required if Integral Value is missing eFMS_CFG_GAS_K_FACTOR_VOLUME

(previously eFMS_CFG_K_FACTOR)

eGMR_CFG_PULSES_PER_SCF
K Factor Required if Integral Value is missing (No corresponding data item) eGMR_PROCESS_VAR_K_FACTOR
Meter Factor Optional eFMS_PV_METER_FACTOR eGMR_PROCESS_VAR_METER_FACTOR
Pulses (Pulse Count) Required if Integral Value is missing eFMS_PV_PULSES eGMR_PROCESS_VAR_PULSES
Static Pressure (SP) (Line Pressure) Required if Flowing Pressure Effect is valid eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Back to top

VCone/Wafer Cone (Cone)

The following data items are required for VCone or Wafer Cone calculations for cone devices.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
Atmospheric Pressure Optional, except:

Required if both of the following are true.

  • SP Sensor Type = Gauge
  • Compressibility Calculation = NX 19 GCN or NX 19 Complete
eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Low Flow Cutoff - DP (differential pressure) Optional eFMS_CFG_LOW_FLOW_CUTOFF_DP eGMR_CFG_LOW_FLOW_CUTOFF_DP
Low Flow Cutoff - Flow Rate (volume flow rate) Optional eFMS_CFG_LOW_FLOW_CUTOFF_FLOW_RATE eGMR_CFG_LOW_FLOW_CUTOFF_FLOW_RATE
Cone Diameter Required eFMS_CFG_CONE_DIAMETER eGMR_CFG_CONE_DIAMETER
Cone Material Required to have a valid value (not Unspecified) if Cone Thermal Expansion Coefficient is missing eFMS_CFG_CONE_MATERIAL eGMR_CFG_CONE_MATERIAL
Cone Reference Temperature Required eFMS_CFG_CONE_REF_TEMP eGMR_CFG_CONE_DIAMETER_MEASURE_TEMP
Cone Thermal Expansion Coefficient Required if Cone Material = Unspecified eFMS_CFG_CONE_COEFFICIENT_THERMAL_EXPANSION (No corresponding data item)
Discharge Coefficient Required eFMS_CFG_DISCHARGE_COEFFICIENT eGMR_CFG_DISCHARGE_COEFFICIENT
Fluid Type Optional eFMS_CFG_FLUID_TYPE eGMR_CFG_FLUID_TYPE
Heating Value - Volume Optional eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Isentropic Exponent Optional eFMS_CFG_ISENTROPIC_EXPONENT eGMR_CFG_ISENTROPIC_EXPONENT
Meter Factor Optional eFMS_CFG_METER_FACTOR eGMR_CFG_METER_CORRECTION_FACTOR
Meter Tube Inside Diameter Required eFMS_CFG_METER_TUBE_INSIDE_DIAMETER eGMR_CFG_INSIDE_PIPE_DIAMETER
Meter Tube Material Required to have a valid value (not Unspecified) if Pipe Thermal Expansion Coefficient is missing eFMS_CFG_METER_TUBE_MATERIAL eGMR_CFG_PIPE_MATERIAL
Meter Tube Reference Temperature Required eFMS_CFG_METER_TUBE_REF_TEMP eGMR_CFG_INSIDE_PIPE_DIAMETER_MEASURE_TEMP
Pipe Thermal Expansion Coefficient Required if Pipe/Meter Tube Material = Unspecified eFMS_CFG_PIPE_COEFFICIENT_THERMAL_EXPANSION eGMR_CFG_PIPE_EXPANSION_FACTOR
SP Sensor Type Required eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
Water Vapor Correction Factor Optional eFMS_CFG_WATER_VAPOR_CORRECTION_FACTOR eGMR_CFG_CALC_WATER_VAPOR_CORRECTION_FACTOR
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Differential Pressure (DP) Required eFMS_PV_DIFF_PRESSURE eGMR_PROCESS_VAR_DIFF_PRESSURE
Static Pressure (SP) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Flow Time Required eFMS_PV_FLOW_TIME eGMR_PROCESS_VAR_FLOW_TIME
Discharge Coefficient Required eFMS_PV_DISCHARGE_COEFFICIENT (No corresponding data item)
Heating Value - Volume Optional eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Meter Factor Optional eFMS_PV_METER_FACTOR eGMR_PROCESS_VAR_METER_FACTOR
Back to top

AGA-8 Detailed

The following data items are required for AGA 8 (Detailed method) compressibility calculations.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
AGA 8 Expanded Range Optional

See AGA 8 Data Ranges for more information.

eFMS_CFG_AGA8_EXPANDED_RANGE eGMR_CFG_AGA8_EXPANDED_RANGE
Atmospheric Pressure Required if SP Sensor Type = Gauge eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
Methane

 

 

 

 

 

 

 

Required if corresponding History item is missing

eFMS_CFG_METHANE eGMR_CFG_PERCENTAGE_OF_METHANE
Ethane eFMS_CFG_ETHANE eGMR_CFG_PERCENTAGE_OF_ETHANE
Propane eFMS_CFG_PROPANE eGMR_CFG_PERCENTAGE_OF_PROPANE
Isobutane eFMS_CFG_ISOBUTANE eGMR_CFG_PERCENTAGE_OF_ISOBUTANE
n-Butane eFMS_CFG_N_BUTANE eGMR_CFG_PERCENTAGE_OF_N_BUTANE
Isopentane eFMS_CFG_ISOPENTANE eGMR_CFG_PERCENTAGE_OF_ISOPENTANE
n-Pentane eFMS_CFG_N_PENTANE eGMR_CFG_PERCENTAGE_OF_N_PENTANE
Neopentane eFMS_CFG_NEO_PENTANE eGMR_CFG_PERCENTAGE_OF_NEO_PENTANE
n-Hexane eFMS_CFG_N_HEXANE eGMR_CFG_PERCENTAGE_OF_N_HEXANE
n-Heptane eFMS_CFG_N_HEPTANE eGMR_CFG_PERCENTAGE_OF_N_HEPTANE
n-Octane eFMS_CFG_N_OCTANE eGMR_CFG_PERCENTAGE_OF_N_OCTANE
n-Nonane eFMS_CFG_N_NONANE eGMR_CFG_PERCENTAGE_OF_N_NONANE
n-Decane eFMS_CFG_N_DECANE eGMR_CFG_PERCENTAGE_OF_N_DECANE
Nitrogen eFMS_CFG_NITROGEN eGMR_CFG_PERCENTAGE_OF_NITROGEN
Carbon Dioxide eFMS_CFG_CARBON_DIOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_DIOXIDE
Water eFMS_CFG_WATER eGMR_CFG_PERCENTAGE_OF_WATER
Hydrogen Sulfide eFMS_CFG_HYDROGEN_SULFIDE eGMR_CFG_PERCENTAGE_OF_HYDROGEN_SULFIDE
Hydrogen eFMS_CFG_HYDROGEN eGMR_CFG_PERCENTAGE_OF_HYDROGEN
Carbon Monoxide eFMS_CFG_CARBON_MONOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_MONOXIDE
Oxygen eFMS_CFG_OXYGEN eGMR_CFG_PERCENTAGE_OF_OXYGEN
Helium eFMS_CFG_HELIUM eGMR_CFG_PERCENTAGE_OF_HELIUM
Argon eFMS_CFG_ARGON eGMR_CFG_PERCENTAGE_OF_ARGON
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Static Pressure (SP) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Methane

 

 

 

 

 

 

 

Required if corresponding Configuration item is missing

eFMS_PV_METHANE eGMR_PROCESS_VAR_METHANE
Ethane eFMS_PV_ETHANE eGMR_PROCESS_VAR_ETHANE
Propane eFMS_PV_PROPANE eGMR_PROCESS_VAR_PROPANE
Isobutane eFMS_PV_ISOBUTANE eGMR_PROCESS_VAR_ISOBUTANE
n-Butane eFMS_PV_N_BUTANE eGMR_PROCESS_VAR_N_BUTANE
Isopentane eFMS_PV_ISOPENTANE eGMR_PROCESS_VAR_ISOPENTANE
n-Pentane eFMS_PV_N_PENTANE eGMR_PROCESS_VAR_N_PENTANE
Neopentane eFMS_PV_NEO_PENTANE eGMR_PROCESS_VAR_NEO_PENTANE
n-Hexane eFMS_PV_N_HEXANE eGMR_PROCESS_VAR_N_HEXANE
n-Heptane eFMS_PV_N_HEPTANE eGMR_PROCESS_VAR_N_HEPTANE
n-Octane eFMS_PV_N_OCTANE eGMR_PROCESS_VAR_N_OCTANE
n-Nonane eFMS_PV_N_NONANE eGMR_PROCESS_VAR_N_NONANE
n-Decane eFMS_PV_N_DECANE eGMR_PROCESS_VAR_N_DECANE
Nitrogen eFMS_PV_NITROGEN eGMR_PROCESS_VAR_NITROGEN
Carbon Dioxide eFMS_PV_CARBON_DIOXIDE eGMR_PROCESS_VAR_CARBON_DIOXIDE
Water eFMS_PV_WATER eGMR_PROCESS_VAR_WATER
Hydrogen Sulfide eFMS_PV_HYDROGEN_SULFIDE eGMR_PROCESS_VAR_HYDROGEN_SULFIDE
Hydrogen eFMS_PV_HYDROGEN eGMR_PROCESS_VAR_HYDROGEN
Carbon Monoxide eFMS_PV_CARBON_MONOXIDE eGMR_PROCESS_VAR_CARBON_MONOXIDE
Oxygen eFMS_PV_OXYGEN eGMR_PROCESS_VAR_OXYGEN
Helium eFMS_PV_HELIUM eGMR_PROCESS_VAR_HELIUM
Argon eFMS_PV_ARGON eGMR_PROCESS_VAR_ARGON
Back to top

AGA-8 Gross 1 & 2

The following data items are required for AGA 8 (Gross 1 & 2 method) compressibility calculations.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
AGA 8 Expanded Range Optional

See AGA 8 Data Ranges for more information.

eFMS_CFG_AGA8_EXPANDED_RANGE eGMR_CFG_AGA8_EXPANDED_RANGE
Atmospheric Pressure Required if SP Sensor Type = Gauge eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Heating Value - Volume Required if corresponding history item is missing eFMS_CFG_HEATING_VALUE_VOLUME (No corresponding data item)
Relative Density Required if corresponding history item is missing eFMS_CFG_RELATIVE_DENSITY eGMR_CFG_SPECIFIC_GRAVITY
SP Sensor Type Optional eFMS_CFG_SP_SENSOR_TYPE (No corresponding data item)
% of Carbon Dioxide

 

Required if corresponding History item is missing

eFMS_CFG_CARBON_DIOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_DIOXIDE
% of Carbon Monoxide eFMS_CFG_CARBON_MONOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_MONOXIDE
% of Hydrogen eFMS_CFG_HYDROGEN eGMR_CFG_PERCENTAGE_OF_HYDROGEN
% of Methane eFMS_CFG_METHANE eGMR_CFG_PERCENTAGE_OF_METHANE
% of Nitrogen eFMS_CFG_NITROGEN eGMR_CFG_PERCENTAGE_OF_NITROGEN
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Heating Value - Volume Required eFMS_PV_HEATING_VALUE_VOL eGMR_PROCESS_VAR_HEATING_VALUE
Relative Density Required eFMS_PV_RELATIVE_DENSITY eGMR_PROCESS_VAR_SPECIFIC_GRAVITY
Static Pressure (SP) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
% of Carbon Dioxide

 

Required if corresponding Configuration item is missing

eFMS_PV_CARBON_DIOXIDE eGMR_PROCESS_VAR_CARBON_DIOXIDE
% of Carbon Monoxide eFMS_PV_CARBON_MONOXIDE eGMR_PROCESS_VAR_CARBON_MONOXIDE
% of Hydrogen eFMS_PV_HYDROGEN eGMR_PROCESS_VAR_HYDROGEN
% of Methane eFMS_PV_METHANE eGMR_PROCESS_VAR_METHANE
% of Nitrogen eFMS_PV_NITROGEN eGMR_PROCESS_VAR_NITROGEN
Back to top

NX-19 Complete

The following data items are required for NX 19 Complete (Complete method) compressibility calculations.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
Atmospheric Pressure Optional eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Relative Density Required if corresponding history item is missing eFMS_CFG_RELATIVE_DENSITY eGMR_CFG_SPECIFIC_GRAVITY
Methane

 

 

 

 

 

 

 

Required if corresponding History item is missing

eFMS_CFG_METHANE eGMR_CFG_PERCENTAGE_OF_METHANE
Ethane eFMS_CFG_ETHANE eGMR_CFG_PERCENTAGE_OF_ETHANE
Propane eFMS_CFG_PROPANE eGMR_CFG_PERCENTAGE_OF_PROPANE
Isobutane eFMS_CFG_ISOBUTANE eGMR_CFG_PERCENTAGE_OF_ISOBUTANE
n-Butane eFMS_CFG_N_BUTANE eGMR_CFG_PERCENTAGE_OF_N_BUTANE
Isopentane eFMS_CFG_ISOPENTANE eGMR_CFG_PERCENTAGE_OF_ISOPENTANE
n-Pentane eFMS_CFG_N_PENTANE eGMR_CFG_PERCENTAGE_OF_N_PENTANE
Neopentane eFMS_CFG_NEO_PENTANE eGMR_CFG_PERCENTAGE_OF_NEO_PENTANE
n-Hexane eFMS_CFG_N_HEXANE eGMR_CFG_PERCENTAGE_OF_N_HEXANE
n-Heptane eFMS_CFG_N_HEPTANE eGMR_CFG_PERCENTAGE_OF_N_HEPTANE
n-Octane eFMS_CFG_N_OCTANE eGMR_CFG_PERCENTAGE_OF_N_OCTANE
n-Nonane eFMS_CFG_N_NONANE eGMR_CFG_PERCENTAGE_OF_N_NONANE
n-Decane eFMS_CFG_N_DECANE eGMR_CFG_PERCENTAGE_OF_N_DECANE
Nitrogen eFMS_CFG_NITROGEN eGMR_CFG_PERCENTAGE_OF_NITROGEN
Carbon Dioxide eFMS_CFG_CARBON_DIOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_DIOXIDE
Water eFMS_CFG_WATER eGMR_CFG_PERCENTAGE_OF_WATER
Hydrogen Sulfide eFMS_CFG_HYDROGEN_SULFIDE eGMR_CFG_PERCENTAGE_OF_HYDROGEN_SULFIDE
Hydrogen eFMS_CFG_HYDROGEN eGMR_CFG_PERCENTAGE_OF_HYDROGEN
Carbon Monoxide eFMS_CFG_CARBON_MONOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_MONOXIDE
Oxygen eFMS_CFG_OXYGEN eGMR_CFG_PERCENTAGE_OF_OXYGEN
Helium eFMS_CFG_HELIUM eGMR_CFG_PERCENTAGE_OF_HELIUM
Argon eFMS_CFG_ARGON eGMR_CFG_PERCENTAGE_OF_ARGON
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Relative Density Required if corresponding configuration item is missing eFMS_PV_RELATIVE_DENSITY eGMR_PROCESS_VAR_SPECIFIC_GRAVITY
Static Pressure (SP) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Methane

 

 

 

 

 

 

 

Required if corresponding Configuration item is missing

eFMS_PV_METHANE eGMR_CFG_PERCENTAGE_OF_METHANE
Ethane eFMS_PV_ETHANE eGMR_CFG_PERCENTAGE_OF_ETHANE
Propane eFMS_PV_PROPANE eGMR_CFG_PERCENTAGE_OF_PROPANE
Isobutane eFMS_PV_ISOBUTANE eGMR_CFG_PERCENTAGE_OF_ISOBUTANE
n-Butane eFMS_PV_N_BUTANE eGMR_CFG_PERCENTAGE_OF_N_BUTANE
Isopentane eFMS_PV_ISOPENTANE eGMR_CFG_PERCENTAGE_OF_ISOPENTANE
n-Pentane eFMS_PV_N_PENTANE eGMR_CFG_PERCENTAGE_OF_N_PENTANE
Neopentane eFMS_PV_NEO_PENTANE eGMR_CFG_PERCENTAGE_OF_NEO_PENTANE
n-Hexane eFMS_PV_N_HEXANE eGMR_CFG_PERCENTAGE_OF_N_HEXANE
n-Heptane eFMS_PV_N_HEPTANE eGMR_CFG_PERCENTAGE_OF_N_HEPTANE
n-Octane eFMS_PV_N_OCTANE eGMR_CFG_PERCENTAGE_OF_N_OCTANE
n-Nonane eFMS_PV_N_NONANE eGMR_CFG_PERCENTAGE_OF_N_NONANE
n-Decane eFMS_PV_N_DECANE eGMR_CFG_PERCENTAGE_OF_N_DECANE
Nitrogen eFMS_PV_NITROGEN eGMR_CFG_PERCENTAGE_OF_NITROGEN
Carbon Dioxide eFMS_PV_CARBON_DIOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_DIOXIDE
Water eFMS_PV_WATER eGMR_CFG_PERCENTAGE_OF_WATER
Hydrogen Sulfide eFMS_PV_HYDROGEN_SULFIDE eGMR_CFG_PERCENTAGE_OF_HYDROGEN_SULFIDE
Hydrogen eFMS_PV_HYDROGEN eGMR_CFG_PERCENTAGE_OF_HYDROGEN
Carbon Monoxide eFMS_PV_CARBON_MONOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_MONOXIDE
Oxygen eFMS_PV_OXYGEN eGMR_CFG_PERCENTAGE_OF_OXYGEN
Helium eFMS_PV_HELIUM eGMR_CFG_PERCENTAGE_OF_HELIUM
Argon eFMS_PV_ARGON eGMR_CFG_PERCENTAGE_OF_ARGON
Back to top

NX-19 GCN

The following data items are required for NX 19 GCN (Gravity/Carbon/Nitrogen method) compressibility calculations.

Note: Some data items are listed as "optional" in this list of "required" items. While these data items are not specifically required to have values, they will be used in the calculation if provided.

Data Item Description Input Required FMS Data Item String FMS Legacy Data Item String
Configuration Items See FMS Configuration Data Items and FMS Legacy Configuration Data Items for more information.
Atmospheric Pressure Optional eFMS_CFG_ATMOSPHERIC_PRESSURE eGMR_CFG_ATMOSPHERIC_PRESSURE
Base Pressure Required eFMS_CFG_BASE_PRESSURE eGMR_CFG_CONTRACT_PRESSURE
Base Temperature Required eFMS_CFG_BASE_TEMPERATURE eGMR_CFG_CONTRACT_TEMPERATURE
Relative Density Required if corresponding history item is missing eFMS_CFG_RELATIVE_DENSITY eGMR_CFG_SPECIFIC_GRAVITY
Methane Required if not using legacy Line Pack calculations, and if corresponding history item is missing eFMS_CFG_METHANE eGMR_CFG_PERCENTAGE_OF_METHANE
Nitrogen Required if corresponding history item is missing eFMS_CFG_NITROGEN eGMR_CFG_PERCENTAGE_OF_NITROGEN
Carbon Dioxide eFMS_CFG_CARBON_DIOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_DIOXIDE
History Items See FMS History Data Items and FMS Legacy History Data Items for more information.
Flow Temperature Required eFMS_PV_FLOW_TEMP eGMR_PROCESS_VAR_FLOW_TEMP
Relative Density Required if corresponding configuration item is missing eFMS_PV_RELATIVE_DENSITY eGMR_PROCESS_VAR_SPECIFIC_GRAVITY
Static Pressure (SP) (Line Pressure) Required eFMS_PV_LINE_PRESSURE eGMR_PROCESS_VAR_LINE_PRESSURE
Methane Required if not using legacy Line Pack calculations, and corresponding configuration item is missing eFMS_PV_METHANE eGMR_CFG_PERCENTAGE_OF_METHANE
Nitrogen Required if corresponding configuration item is missing eFMS_PV_NITROGEN eGMR_CFG_PERCENTAGE_OF_NITROGEN
Carbon Dioxide eFMS_PV_CARBON_DIOXIDE eGMR_CFG_PERCENTAGE_OF_CARBON_DIOXIDE